B-Vent

Kevin_54
Member Posts: 30
I was wondering if anyone could tell me what the difference is between B-Vent and Type L doublewall?
0
Comments
-
\"L-vent\"
can be used for oil- or gas-fired units, whereas "B-vent" can only be used with gas.
L-vent is more expensive, but wouldn't need replacing if you switch fuels.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks
Thank you. You said there is a price difference. Im guessing this is due to the type of materials used?0 -
L vent
Type L vent is listed to UL 641 and was originally developed for oil. However, most L-vent is now sold for use with pellet stoves. The inner liner is 300 series stainless steel whereas B-vent uses 6006 aluminum. The outer jacket may be galvanized steel, Galvalume or stainless steel. Lvent has a fiberglass rope packing in the female end. L-vent is rated for 560F and a higher corrosion resistance than B-vent, which is listed to UL 441 and rated for 480F. The clearance on Lvent varies from 1-3 inches for most brands while B-vent is 1".
You must use the same brand of components and not mix & match.
HTH,0 -
Thanks
Knowledge is power! Thanks for the thorough explanation.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 159 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 942 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements