Richardson system ball check union

Chris F.
Member Posts: 1
I have a 2 pipe steam richardson system radiator that will not heat. The supply will start to get hot, but not the sections. I removed the ball check union, but it has no ball in it. can I replace it with a steam trap,and replace the graduated supply valve with a standard supply valve? some of the newer radiators are connected this way.
0
Comments
-
Yes....
But if it is working leave the graduated valve in place. Many of them still work well after all these years. A Tunstall or Hoffman trap will work. Mad Dog