Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
wiring question
carol_3
Member Posts: 397
Have you tried going to the manufacturer's website for schematics?
0
Comments
-
control question
HELLO ALL, I WANT TO KNOW IF YOU CAN WIRE IN A WF2-24 SERIES AUTO WATER FEEDER WITH A SERIES 47 (MCDONNEL MILLER)LOW WATER CUTOFF. I HAVE NEVER COME ACROSS A 47 UNTILL NOW. SCEMATICS ANY ONE. THANKS.0 -
47 is a combo LWCO and mechanical feeder,
and as best I can tell, you cannot due to there being only one set of contacts designed for burner operation cut out only.
Here is a link to the 47 manual:
http://www.mcdonnellmiller.com/pdf/install_instr/MM-316B.pdf0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements