wiring question

Have you tried going to the manufacturer's website for schematics?

Comments

  • tom k_5
    tom k_5 Member Posts: 12
    control question

    HELLO ALL, I WANT TO KNOW IF YOU CAN WIRE IN A WF2-24 SERIES AUTO WATER FEEDER WITH A SERIES 47 (MCDONNEL MILLER)LOW WATER CUTOFF. I HAVE NEVER COME ACROSS A 47 UNTILL NOW. SCEMATICS ANY ONE. THANKS.
  • Glenn Harrison_2
    Glenn Harrison_2 Member Posts: 845
    47 is a combo LWCO and mechanical feeder,

    and as best I can tell, you cannot due to there being only one set of contacts designed for burner operation cut out only.

    Here is a link to the 47 manual:

    http://www.mcdonnellmiller.com/pdf/install_instr/MM-316B.pdf