control question
HELLO ALL, I WANT TO KNOW IF YOU CAN WIRE IN A WF2-24 SERIES AUTO WATER FEEDER WITH A SERIES 47 (MCDONNEL MILLER)LOW WATER CUTOFF. I HAVE NEVER COME ACROSS A 47 UNTILL NOW. SCEMATICS ANY ONE. THANKS.0 -
47 is a combo LWCO and mechanical feeder,
and as best I can tell, you cannot due to there being only one set of contacts designed for burner operation cut out only.
Here is a link to the 47 manual:
http://www.mcdonnellmiller.com/pdf/install_instr/MM-316B.pdf0