System pressure
Ryan_14
Member Posts: 8
We have a system that we have inherited. A copper tube boiler heating an indirect heater which holds agricultural product. The system pump is on the return. We are getting a 10 pound difference in pressure on the inlet side of the pump and the outlet of the boiler. I have not seen this before. Isn't this a bit unusual? Customer installed gauges and has questioned me to as why this is.
0
Comments
-
\"Agricultural Product\"
That is a good euphemism. I will have to remember that next time the DEA is in town
Is the circulator pumping away from the expansion tank? Is the difference in pressure negative or positive and where is it being measured...
If you are pumping TO the expansion tank, the suction pressure will drop about the entire pump head value. If you are pumping away from the expansion tank, the discharge pressure will increase as a function of the system resistance at that flow point.
Depending on the system, flow rates, pipe sizes, having that kind of pressure would be unusual (high) in a home heating system and normal if not low in some industrial or commercial applications.
A diagram might help.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements