I have a customer with a Capitol 25-5 boiler. The boiler inspector wants to know the minimum relief valve capacity. I was wondering if anyone had any actual factory information more than just using how it is fired today.

Comments

  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    I would assume

    it's a rather large boiler since it requires inspection. There were several Capitol 25-5 boilers made back in the day, the largest of which had a rating of 1375 square feet of steam radiation. You'd probably fire this one at something like 4 GPH on oil, which equals an input of 560,000 BTU per hour.

    This is probably the number the inspector would want.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Tom Byrley's

    Hydronic Rating Handbook gives the Capitol 25B (25-5) a NET steam rating of 1,265 sq ' or 303,600 btus. Before 1958, when that boiler was built, NET was 68% of GROSS output. Or 446,500 btus.