EDR calculations at different temperatures

Brad White_9
Brad White_9 Member Posts: 2,440
Dave is right- Radiation is not heat loss.

As Dave said, knowing your heat loss is primary; knowing your radiation is secondary and tells you how lucky you probably are to run "X" temperature on a design day.

As for de-rating, (assuming that your starting point of 170 degree average water temperature yields 150 BTUH per SF right?) it is this easy:

Subtract 20 BTU's per EDR for every 10 degree drop in average water temperature, assuming a 70 degree room.

So your 150 BTUH at 170 degree AWT becomes:

130 BTUH @ 160F AWT

110 BTUH @ 150F AWT, etc. etc.

Down to 10 BTUH @ 100F AWT

Comments

  • Dave_4
    Dave_4 Member Posts: 1,405
    EDR calculations at different temperatures

    Hello,
    I have done a total EDR calculation based upon the data I found on this webpage at an avg temp of 170F. If the avg temp in my system is less than 170F, how do I do the calculation? Is there an equation or another table at different temperatures?

    Thanks.
  • bert
    bert Member Posts: 50
    edr graph

    Here is something you might use.
    If I attached it correctly.
  • Be very careful here,

    I would be "very leery" of sizing a HW replacement boiler by the existing EDR alone,,,the only real accuracy is in doing a room by room heat-loss calculation. That way you`ll know the exact water temp. you need in these (possibly now) oversized rads.

    Dave
  • Glenn Sossin_2
    Glenn Sossin_2 Member Posts: 592


  • Glenn Sossin_2
    Glenn Sossin_2 Member Posts: 592
    graph

    Don't see it Unless of course my glasses are still dirty