EDR calculations at different temperatures
Brad White_9
Member Posts: 2,440
Dave is right- Radiation is not heat loss.
As Dave said, knowing your heat loss is primary; knowing your radiation is secondary and tells you how lucky you probably are to run "X" temperature on a design day.
As for de-rating, (assuming that your starting point of 170 degree average water temperature yields 150 BTUH per SF right?) it is this easy:
Subtract 20 BTU's per EDR for every 10 degree drop in average water temperature, assuming a 70 degree room.
So your 150 BTUH at 170 degree AWT becomes:
130 BTUH @ 160F AWT
110 BTUH @ 150F AWT, etc. etc.
Down to 10 BTUH @ 100F AWT
As Dave said, knowing your heat loss is primary; knowing your radiation is secondary and tells you how lucky you probably are to run "X" temperature on a design day.
As for de-rating, (assuming that your starting point of 170 degree average water temperature yields 150 BTUH per SF right?) it is this easy:
Subtract 20 BTU's per EDR for every 10 degree drop in average water temperature, assuming a 70 degree room.
So your 150 BTUH at 170 degree AWT becomes:
130 BTUH @ 160F AWT
110 BTUH @ 150F AWT, etc. etc.
Down to 10 BTUH @ 100F AWT
0
Comments
-
EDR calculations at different temperatures
Hello,
I have done a total EDR calculation based upon the data I found on this webpage at an avg temp of 170F. If the avg temp in my system is less than 170F, how do I do the calculation? Is there an equation or another table at different temperatures?
Thanks.0 -
edr graph
Here is something you might use.
If I attached it correctly.0 -
Be very careful here,
I would be "very leery" of sizing a HW replacement boiler by the existing EDR alone,,,the only real accuracy is in doing a room by room heat-loss calculation. That way you`ll know the exact water temp. you need in these (possibly now) oversized rads.
Dave0 -
0 -
graph
Don't see it Unless of course my glasses are still dirty0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements