feet of head
he already got that ED, he had posted a few times under different names, you know how it goes.<BR><BR>Dave
0
Comments
-
feet of head
the longest zone is 258' it`s btu/hr is15000, the 127956 btu/hr was the total of all 4 zones added together. I have this formula from my IBR manual, but its been a while since I took algebra. head Loss=(258/100)x.274x(13)1.75 the 258 is my length, divided by 100' x this # I got from my manual and relates to the 3/4 pipe used(.274)the last part i can`t figure out, the 1.75 is acually up in the right hand corner of the 13 , if it was a 2 up there I think it would be 13x13 , you know , squared but what do I do with the 1.75 in this equation0 -
> the longest zone is 258' it`s btu/hr is15000, the
> 127956 btu/hr was the total of all 4 zones added
> together. I have this formula from my IBR manual,
> but its been a while since I took algebra. head
> Loss=(258/100)x.274x(13)1.75 the 258 is my
> length, divided by 100' x this # I got from my
> manual and relates to the 3/4 pipe used(.274)the
> last part i can`t figure out, the 1.75 is acually
> up in the right hand corner of the 13 , if it was
> a 2 up there I think it would be 13x13 , you know
> , squared but what do I do with the 1.75 in this
> equation
0 -
........
What is your question ....0 -
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements