propane line
Options
kev
Member Posts: 100
I am trying to determine the max amount of cubic feet of propane that can be moved through a 1/2" OD copper line from the storage tank to the second stage regulator. Not sure at what pressure first stage regulator normaly is set. The run is about twelve feet. Thanks.
0
Comments
-
PSI
The answer is.... It depends on the pressure of the 1st regulator. You would have to know that number. Those are adjustable, by the way, within a certain range. The higher the pressure, the more CFM you can pass through 1/2 inch pipe......0 -
If the first stage is set at 10 psi
You should be able to feed nearly 2 million btu thru 1/2 inch for 12 feet. It all goes away after the second stage reg; if set at 11 inches WC you would need to jump up to 1 and 1/2 inch (steel) and not exceed 30 feet developed length to maintain that kind of load. (from the 2003 IFGC)0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements