Dunham vapor Sys needs help
Steamhead (in transit)
Member Posts: 6,688
should appear on the top. Tunstall and Barnes & Jones both make replacement elements for Dunham traps.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Dunham Vapor Sys in Pottsville needs help
Having fallen in love with steam heat, I read the WALL every day and I purchased Dan's books. I am in the AC/R industry. I recently specified a steam boiler replacement for my mom's house and that system - a RICHARDSON system - is cadillacin'.
There is a DUNHAM VAPOR System - two pipe of course - in this old mansion that was converted into 5 apartments. My sweetheart lives in one of them - she's been there 10 years. I have been studying the system and reported here about its condition. Advice from the WALL was that I should say something to the landlord.
Well, we talked and he is very enthusastic about making improvements. He burns a lot of coal he said. He is a very good community guy and a good landlord, and as you will see, certainly can use some help, so I'd like to help. I could use some advice from the Wall.
System deficiencies:
The most obvious problem is the venting. Vents were added to many of the radiators, which we know from Dan H, is a No-NO. I never feel air escaping from the main vent.
I could feel steam entering some of the return lines.
Distribution/regulation is hampered because many inlet valves are very tight and missing handles. Hence, the occupants cannot control anything. Windows get opened to regulate the temp...
The mossy looking stuff on the boiler tubes looks a bit heavy. I am sure it impedes heat transfer. Anybody have experience with this? Is it that heavy from just one season? The boiler is 'serviced' once a year -they clean 'something' I am told...
STEPS TO IMPROVE OPERATION:
Here is where I could use some advice... I know just enough to be dangerous...my approach would be:
1. I would inspect the main vent to make sure it can vent.
2. I would plan on replacing all the steam traps.
3. Remove the air vents on the radiators.
4. Free up the inlet valves.
5. Put a proper gauge on the boiler - say 0-3 PSI.
6. Clean the moss off the boiler surface.
7. Have a beer.
Then the next day.... ha ha ha just kidding you guys.
I can post other photos of the crossover vents (2) and the poor vaporstat and other details separately or as requested.
The system does heat of course and water level in the gauge glass is normal.
How would some of you wise and experienced men approach this improvement challenge?
Thanks,
Coal Cracker Paul0 -
There is a certain minimum amount of maintenance required on all steam systems, weekly and periodically. Steam traps usually find themselves in the periodic category. Unfortunately, periods can be quite long, and viewed as an "all or nothing" venture. They get deferred frequently. There can be other alternatives to this, however.
There is nothing as easy as deciding to change every single trap and calling it cured, except not doing anything. Those are usually the two choices presented. The third choice is pretty labor intensive. It involves identifying exactly what is installed in the building, what is wrong with it, what it would take to fix it (broken down in stages), and what order to do it in, and what each stage would accomplish and cost.
This would chip expectations down to manageable and budgetable projects, and might give incentives to combine steps where it would save money to do so. It would help project for future budgets what the actual maintenance costs are on a large building with a seventy five year old heating system. It would maintain fuel consumption at predictable levels.
It would show how thrifty it is to keep up with steam trap maintenance. I'd like to help discover how to do this in laymans terms. My experience is with four story brick residences with various vapor systems from 1910 through the 1960s. These were mostly two pipe vapor systems.
The very first thing to do is to identify the individual steps in an outline form that will bring the system back to working properly. Identify the system from trap names, unusual items in the returns or near the boiler, supply valve names, something to date the system with. This helps a little. Identify the height above the boiler water line to the lowest horizontal piping in the whole system that is above it. This is a B dimension, and is most important if there isn't a vented condensate tank or boiler feed tank. It defines what pressure the system was meant to be run at. Identify what vent is on the system and if it works, and at what rate it vents.
The first thing to address on the outline would be venting, as it has the biggest payback to cost ratio. Simply size the vent properly for the load and pipe lengths, and make sure it vents when it is cold, and it shuts when it gets hot. Make sure it is back from the end of the main about a foot or two, or more. It can even be right after the last radiator connects to the return main. There is likely to be a crossover pipe between the supply main and the return main there, with a radiator trap as the union and elbow on the return end. This is the supply main's air vent into the return. This flow is from supply to return to air vent. To keep the air and condensate all flowing the same way, the vent will be downstream and downhill from this crossover connection.
The next item on the outline will be to crank the pressure down to the pressure just above what it takes to get the main air vent to close. Identify that the control on the boiler might eventually need to be replaced with the one required to run this particular system at the design pressure. More on this later.
The next item to successfully tame the system is going to be insulation on all of the pipes. It simply must be in good shape to deliver all of the steam that they were designed to carry. If the steam condenses within the mains, the cross section of the pipe becomes reduced and the mains cannot carry the steam that they need to at reasonable velocities. The speed picks up and the water starts flying around, the noise goes up, the cost to run goes up, the vents and traps get hammered into little crumpled balls of metal inside. The insulation is mandatory. The mains are actually TWO pipe sizes too small, if the pipes are bare.
Along with insulating, the boiler piping must be right before the insulation gets applied. The first thing to do is to determine what the boiler needs to do, and if it will. We finally have come down to measuring the load connected to the boiler, and the size of the boiler, and to actually verify the firing rate and combustion efficiency. A filthy oil boiler that had been downfired beyond reason won't show up from a peek at the rating plate. It might make sense to look at the boiler size itself and it's piping, and start from scratch. It might be fine. Be sure the boiler piping matches the manufacturer's instructions, to the letter. Undersized piping might be the problem. Now is the time to decide.
If you have come this far, and have a working system to evaluate the steam traps with, you can move to the next step on the outline. You need a trap survey; a document that you make that shows what each trap model number is, and what room it is in. You need to group them by which branch of the RETURN main that they empty into. The return mains are groups of traps to be maintained and troubleshot as a group. It helps to begin thinking of them that way early. Along with this list of traps, a piping plan would be wonderful. These documents should be filed in a way that they outlast you on the job.
Once you have identified a return main, and have the steam pressure cranked down as low as it will go, start the system up cold and see if the return main becomes steam hot at the vent, up on this end of the return. Since only air is supposed to be there, and cooler condensate, it should remain open and not be steam hot. If it gets hot within minutes, you have a trap blowing steam through. On a system with working steam traps, and on ALL pumped condensate systems, the vent isn't needed. It only sees steam if a trap lets steam through. An open pipe could serve as the vent.
Take it out, if it isn't too much trouble, while you troubleshoot. It will speed up the whole process. The way that we are going to discuss checking traps isn't the only way, by any means. My focus is on cost of materials, but admittedly it is very labor intensive. This isn't developing a free estimate for repairs, this is actually a very valuable part of DOING the repairs, and should be thought of this way. The reason for the trap survey in advance is, in part, so that some repair parts for traps can be brought in and kept on hand. This enables repair as the testing evolves.
The premise of this method of testing is to follow the steam as it expands into cool piping in the supply mains, and detect, by external pipe temperature, where the traps let steam pass through. I started by using my hands, but years later, infrared thermometers with laser pointers came along, and they cut the time in half.
Start up the boiler until you detect steam in the returns someplace. Shut off the boiler and follow the hot pipe back to it's source. You'll get near it easily enough; close radiator valves off to eliminate their traps; identify how the steam is blowing into the return. Shut the boiler off often because once everything in that return main becomes hot, the information to be gained is very diluted. Keep everything cool, and squirt steam through by firing the boiler once in a while to keep the path hot. This is more art than science.
After the return main stays cool, because all of it's traps are fixed and holding, or shut off from steam, open up radiators one at a time with the steam on. As you open a radiator, check the return for live steam. Condensate dripping into the return will warm it up. Steam blowing into it will make it a blistering 200° F plus, right away. Shut those back off. Mark those for repair.
Here's another note. On a return that you know has steam blowing into it, shut the boiler off with hot mains, and let the vent pipe draw air in until it stops. With all of the radiators and valves open, start up the system again. As soon as the system vent pipe gets hot, go through the building and find HOT HOT traps on radiators that have COLD or cool sections right next to the radiator trap. This will tell you two things. One, there is obviously steam in that return. Two, THIS TRAP IS WORKING!!! It won't let the air from the radiator into the return, which has an open vent on the other end. It is keeping the radiator from venting. Write this one down on your trap survey as good. Look for more. Cool it down and start it again. Check again. Shut some off in a pattern that makes sense along the return, to determine where the steam is moving around. Some of the radiator valves won't hold steam all the way off, but that's OK. As long as the radiator condenses what it does get, and the last section doesn't get steam hot, you'll be OK. The room will use that heat, anyway. It's temporary. Leave off whatever it takes to keep the returns from having steam in them. For temporary heat, crack open radiator valves to allow half the radiator to get hot, but NOT THE TRAP!!!! Fix the crossover traps and the F&T traps on the mains. Get your vent to be cool while the system runs.
Now make a list of the traps on radiators that are shut off. These are what you need to replace. Leave the radiators with bad traps off in the meantime, or mostly off, to save the remainder of the working traps. Budget your replacement costs, but remember that more will fail as time passes. It will often be fewer than expected, though.
Now that the system is tame, and half shut off, the boiler waterline will be pretty wild, due to overfiring. Get the traps fixed to get the load back on the boiler, and troubleshoot from there. Have a very clean system with clean water. This is a whole different subject, but very important.
If the system floods after it runs, or if it runs out of water and shuts off, suspect plugged returns that are below the water line. Don't waste any time on them, replace them. Pipe them so that you can remove an air vent and flush them with a hose to a drain valve that you put in at the boiler end. Use mud legs to collect debris.
Once you get an intimate knowledge of the system, a loving pat on the air vent while it's running will tell you if you need to check your traps again. It should run at virtually the same temperature all of the time, a little hotter in very cold weather.
If you want real economy, buy a vaporstat that operates from 0-1 PSI, and is graduated in ounces. Install it at the boiler, or even better, at the end of the steam supply main. Wire it to break one leg of the thermostat wire through it, and leave the pressuretrol as is, as a high limit. Set the vaporstat as low as you can and still heat every radiator.
All of this would be done with the service person AND the weekly operator. The more involved with the system that the operator becomes, the more known and less costly will be the maintenance plan.
Along the way, you'll both learn the system. You'll find that return that's ALWAYS hot, no matter what. It'll drive you nuts, looking for the cause. Eventually, you'll find the crossover trap in the wall at the end of the main in the finished basement. It'll be behind a wall hung radiator.
You'll find the F&T trap that works, but it has a 3/4" bypass around it with a very painted plug cock in it; wide open.
You search the building and find two more. Guy's have been rebuilding these traps for 90 years, yet the bypasses never were closed. Originally, this system made heat and electricity by coal, the bypasses are from those days.
I want to close with a story. It is very relevant, and it was costly. It was a four-story residence, and the bottom floor was four feet in the ground. The returns ran around the bottom floor ceiling with the supplies, until they were pitched down to a point 30" above the floor, then the return split into a high and a low return back to the boiler room, the same on both ends of the building. The west end had steam in the front return, as a door on the ends of the building split the returns into a back and a front on each end of the building.
This front, west return had steam in it near the boiler end, the low end. The rooms all had thermostatic radiator valves on the radiator inlets, so each had control. The front door entry was always cool, and the radiator always hot. The next room had his thermostat off, because his room was hot enough, and the trap was hot and the radiator burbled steam into it through this hot trap. The radiator would fill with condensate until the system satisfied, when everything would cool off and drain back to the boiler. He opened and closed his window for temperature control.
The next room had the same hot trap and shut-off thermostat, but he was roasting. He NEVER closed the window. He went away every chance he got. One weekend when he was away, it was very cold. The whole weekend never saw above zero temperatures. The guy in the end room by the door called for no heat. Even with the valve open, no heat would come from the radiator. His walls were FREEZING. The hallway wall, the entryway wall, the outside wall, and the room next-door wall.
The radiator was full of water. No steam could get in. Draining it by shutting off the boiler got the radiator to heat but the room didn't heat well.
The wall to the next room was freezing. Uh - oh. In the maintenance guy went, to check on it. Everything was frozen. Bottles on the dresser had broken. The window was open. The radiator had exploded. He shut it off, shut the window, left the door open and went to call in some help. He was gone for a short while.
The frozen and split 1" sprinkler had thawed out while he was gone. The whole time he was gone, a 1" sprinkler pipe filled the west half of this building. About 11 people lived in the lower level, and they were displaced. The water was a few feet deep. Several people on the next level were also displaced to hotel rooms, until the building was renovated.
The steam traps were repaired right away. The rooms were comfortable, after that.
Noel
0 -
Geez Noel, that is the longest post I've ever read..............
A wealth of info as usual. Gimme a call soon, its been a while...We may need to go by Mr. Genny's. Mad Dog
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
It has, hasn't it?
The Peddler, some afternoon?
Noel0 -
Coal fired Dunham system pics
Here are a few more pics of the system.
0 -
Wow!
An old-style coal boiler, still burning coal to operate a Dunham system. Not surprising we see this in central Pennsylvania, where coal still rules.
In addition to Noel's information, I think we might also have an air venting problem. This is probably why the knuckleheads added vents to those radiators. Your vent trap is the only air vent in that entire system. The vacuum check on the vent trap can be unscrewed to see if it is plugged. If the check or vent trap is plugged, air can't leave the system and the steam will not distribute properly.
If the vacuum check is OK or can be cleaned, I'd put it back in. This system was designed to pull vacuum as the coal fire burned down, increasing its efficiency. If the system were burning oil or gas, vacuum wouldn't work so well.
Let us know how well this grand old system works when you fix it. If you get stuck, we're here to help. And Pottsville isn't that far from Baltimore............
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
crossover vent + trap observations/ test question
Studied this Dunham system a bit this weekend using an infrared thermometer. Discovered one of the crossover vents is leaking steam right back into the return. There are 3 maybe 4 crossovers in the system.
Found one trap not even screwed in - just sitting there.
Since steam traps function in the 180-210 F range, I guess there is no way to see if it works unless you get steam to it...or, build a test station as Dan describes on page 147 in TLA of SH. It can take quite a while to get steam through some of these radiator, perhaps due to other system problems.
Can a simpler stove top method be employed? For example, simply meaure the stroke/length change of the trap as you place it in 200+ F water? How much should the length change? Maybe the test stand removes all those unknowns...maybe not, because the remavable trap portion must be in a proper body each time...Has anyone tried such a test???0 -
The real test
Is does it let steam into the return. You won't know until you put it back in.
The other tests might be valuable, but they take time. I never bothered.
Noel0 -
Paul, you say
"Discovered one of the crossover vents is leaking steam right back into the return".....
That's part of your problem.
The steam leaking into the return pressurizes it, so the normal delta-P (engineer-ese for difference in pressure) doesn't exist. If there's no ΔP, steam will not flow. Fix the crossover- might as well do them all since they're all the same age.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Building pic w Dunham system
Yes, that crossover IS a big part of the venting problem.
I will get brave next weekend and disassemble the main vent device, and remove an easy to reach crossover trap element in order to get info for replacemnt parts.
Attached is a picture of the mansion this Dunham system is in. Note the 12" of snow that arrived Friday, March 17. I drove 75 miles through that storm...the normal 1.5 hour trip turned into 4.5 hours. Oh but she is worth it...0 -
identifying parts and inlet valves
Thanks for the tip Steamhead.
I'll need to use a mirror to see top, but that would be safer at this time rather than removing the cap.
As for the Dunham INLET valves, nearly all are missing the original handle and are very stiff. I had to use a pipe wrench to open one. DO you have any tips on restoring these back to user friendly operation, as that will allow occupants to control the heat, rather than opening windows.0 -
Get in touch with Tunstall
www.tunstall-inc.com
They can rebuild almost anything, and can even upgrade many old valves to TRVs.
Tell them we sent you.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Dunham system
That dose not look like a dunham system or may be whats left of one.
see attachment0 -
Dunham system
That dose not look like a dunham system or may be whats left of one.
see attachment0 -
Dunham system
That dose not look like a dunham system or may be whats left of one.
see attachment0 -
Dunham system
That dose not look like a dunham system or may be whats left of one.
see attachment0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements