buderus high efficency boiler
Mike.C
Member Posts: 43
Nope and have about 8 in. 4 for over a year. Someone yard on it a little too much getting it in or out to fill at startup?
Mike.C
Mike.C
0
Comments
-
buderus high efficency
Has anyone had the condensate trap break at the neck? Boiler is one year old.0 -
was everything supported?
Pics would help. Ain't had that happen but then again, we got nuts with kindorf and supports. Mad Dog0 -
Yes
When GB142 is used for high temp applications there is a possibility that the condensate trap will snap at o-ring. Buderus will replace this free of charge. Take it to your wholesaler. I have see at least 10 come back. And as they said use mineral oil to as a trap seal to eliminate evaporation...
Rick0