buderus high efficency boiler

Mike.C
Mike.C Member Posts: 43
Nope and have about 8 in. 4 for over a year. Someone yard on it a little too much getting it in or out to fill at startup?
Mike.C

Comments

  • wet head in wi
    wet head in wi Member Posts: 1
    buderus high efficency

    Has anyone had the condensate trap break at the neck? Boiler is one year old.
  • Mad Dog!!!!!!!!
    Mad Dog!!!!!!!! Member Posts: 157
    was everything supported?

    Pics would help. Ain't had that happen but then again, we got nuts with kindorf and supports. Mad Dog
  • Supply House Rick
    Supply House Rick Member Posts: 1,399
    Yes

    When GB142 is used for high temp applications there is a possibility that the condensate trap will snap at o-ring. Buderus will replace this free of charge. Take it to your wholesaler. I have see at least 10 come back. And as they said use mineral oil to as a trap seal to eliminate evaporation...

    Rick