Steam to hydronic conversion.
Steamhead (in transit)
Member Posts: 6,688
he's running the risk of leaks. Hot-water runs at over 10 times the pressure of steam, and this WILL find any weak point.
Cracked radiators usually aren't a problem on a steam system. I'd be interested to know how that happened.
I'd restore the steam system. If he has to replace radiators, and is planning to insulate, weatherstrip etc (which he should) the new radiators can be smaller. How much smaller would be determined by a heat-loss calculation.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
Cracked radiators usually aren't a problem on a steam system. I'd be interested to know how that happened.
I'd restore the steam system. If he has to replace radiators, and is planning to insulate, weatherstrip etc (which he should) the new radiators can be smaller. How much smaller would be determined by a heat-loss calculation.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Steam to hydronic conversion.
A friend of mine just bought a house with a new steam boiler. He gutted the walls and celings. He tells me there are multiple problems with the steam piping and radiators. ie. cracked radiators, leaky valves and several capped and removed radiators. I am curious if conversion to hydronic with all new piping is a viable option. Any help is appreciated. Thanks, Dean0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements