Venting Question

Vermonter
Vermonter Member Posts: 57
I've got 3 Hoffman 75's on the big one, 2 on the medium one, and 1 on the small one. Sounds like I'm OVER vented on the smallest main and throwing off my balance?

I'm pretty sure that one of the 6 valves that I'm using is shot, is there a reliable way to test?

Comments

  • Vermonter
    Vermonter Member Posts: 57
    Venting Question

    Is there a rule of thumb for venting mains? Something like "One Hoffman 75 for every 250 cubic inches of air in the main...One Gorton #2 for every 1000..." Etc.

    I've got three mains, one is almost 6 times as big as the smallest!

    I did a little math and the smallest has about 300 cubic inches of air in it, the second has 952 cubic inches, and the biggest has 2088 cubic inches.

    Up until last night I had one Hoffman #75 on each one, now I've got 1, 2, and 3 75's on them respectively (thankfully I had them in the house, they're not cheap.)

    I'm tempted to leave a 75 on the smallest main, and put one Gorton #2 and a Hoffman 75 on the second, and 3 #2's on the third. That should give fairly even venting, but is it enough?
  • In order to answer that

    I'd need to know the length and diameter of each of your steam mains. Not sure if you posted this info before, that's why I asked.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Vermonter
    Vermonter Member Posts: 57
    Length and diameter

    The smallest main:

    62" (5.2 ft.) of 2" pipe
    91" (7.6 ft.) of 1 1/4" pipe

    The other two start as one pipe at the header:

    191" (15.9 ft.) of 2" pipe

    There's then a T, the middle sized one continues:

    94" (7.8 ft.) of 2" pipe
    291" (24.3 ft) of 1 1/4" pipe

    The biggest one continues:

    440" (36.7 ft.) of 2" pipe
    331" (27.6 ft.) of 1 1/4" pipe

    The three come back seprately to the Hartford loop, and the venting is independent. Should I give half of the shared piping venting to each of the two larger mains?

    Hope this is what you were asking for.

    Thanks!
  • That's exactly what I'd do

    using the Master Venting method pioneered by Frank Gerety.

    That means each tee-off from that 15.9-foot main gets 0.4 cubic feet added to it.

    I'd put a Gorton #2 on the longest one, a Hoffman #75 on the medium-length one and a Hoffman #4A on the real short one. If they should need fine-tuning, you'll have some extras available.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • The 4A

    is roughly 1/6 the capacity of the 75. That's why I said to get one. You'd need to go way oversize on the other two to equal a 75 on the shortest one.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Vermonter_3
    Vermonter_3 Member Posts: 21
    Thanks!

    Well no wonder things were out of balance with a single Hoffman 75 on each!

    Thanks again for the advice, I'll let you know how it works out.