Anyone have a table or formula?
Does anyone have a table or a formula to correct natural gas volumes from a given outside temperature to a standardized 15°C / 60°F base?
Google and I have found nada while searching.0 -
No, but Google
has abundant links for other activities leading to an interesting, fulfilling and well examined life.
"If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
Tough to find UniR,
every since you PM`d me, I`ve been looking too! Must be a "deep dark" secret? I can`t believe Brad did not know LOL! Enbridge has their own, but who`s to say?
Dave0 -
I've tried with Enbridge
Technical support's probably completely involved in the customer they accidently blew up. I got hopeful seeing 3 responses - dashed! Thanks guys!!0 -
Sorry Uni R
I`m sure what you seek is out there,,,,Good Luck!(I did try.)
Dave0 -
Look at
the badge on the meter to see if it is marked TC also sometimes the color of the badge (red) indicates temperature compensation. Usually +/-2% from -20ºF to 120ºF based on temperature of the flowing gas. They have a bimetal temperature sensor.0 -
bob
curiosity question, would it make a diff if the meter is inside, or outside the basement?
Dave0 -
thanks bob
There is no temperature compensation on this meter and that's why I'm hoping to find a table or a formula that a gas company would use for calculating it.
107,600 BTU @ 15°F = 1??,??? BTU corrected to 15°C or 60°F0 -
I don't
know if all meters are temp. compensated. I would suspect that the tin meters found in basements are not. You can buy meters with or without temp. compensation. I guess it's up to the local utility and the state commerce commission what is used and where.0 -
Thank You Bob
I was curious for a friend!
Dave0 -
UniR
You'll have to cut me some slack if'n I don't explain this too well. V1/T1=V2/T2 and I think we are looking for V2. If the BTU content of your gas is 1000BTU per CuFt V1 is 107.8 CuFt. The temps have to be in Kelvin so T1 is 255ºK and T2 is 288ºK so you end up deviding 288 by 255 times V1 and get 121.7 CuFt. I think! I better add this is based on gas temp. not out side air temp.0 -
Perfect... thanks.
(15+273.15)/(5+273.15) = 1.036
okay so 1.036 x 107,600 = 111,470 @ 15°C0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements