Buderus boiler sizing
Robert O'Brien
Member Posts: 3,563
Assuming no whirlpool or full body shower,I've never had a problem with DHW ouput with a 115/21.I always use a mixing valve to operate at a higher DHW temp which boosts output among many other health and safety benefits.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=313&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=313&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
To learn more about this professional, click here to visit their ad in Find A Contractor.
0
Comments
-
Buderus boiler sizing
My house is app. 1200sq.ft. My heat loss is app. 47,000 btu's. I would like to purchase a 3-pass buderus with o.a. reset and the buderus 32gallon indirect. The G115-21 seems to fit my needs, however several installers have told me I needed the G115-28 because of the DHW recovery. Indicating that the smaller buderus would not be correct even with priority. None of the installers did a heat loss, I supplied them with the footage of the house. Any help would be appreciated. Thanking you in advance.0 -
Hi,
I run a Buderus G115-21 with an LT-160 indirect and it is severly OVERSIZED. It all depends on your heat loss.
I also allways use a mixing valve, run the indirect at higher temperatures and make sure that the indirect's aquastat can be set to a wide differential for less burner cycling.0 -
First Thing To Do...
Is to hire a Contractor to professionally perform Heat Loss Calculations and to size your Domestic Hot Water Tank. This is ALWAYS ALWAYS ALWAYS your best move. What did they base the 47,000 btus on? How do you know this is correct? You will never know at this rate.
You could get advice all day long here,BUT if your system doesn't work properly who can you hold accountable? Not anybody here...
Best of luck to you. (why are you hiding your email?)
My 2-cents
Rick0 -
I would dare bet..........
Your heat loss is even lower than 47K. That equals roughly 40 btu's / sq ft. A LOT of heat loss for that space unless it's built like a chicken koop or your design temp is -50*. Assuming a more normal heat loss of 25-30/ sq ft, your load would be in the 30 to 36K. The 21 will do just fine if that's the case. Don't worry about the DHW output unless you have one of those human car wash showers that flow 10+gpm. You can run the tank hotter and add a mix valve as suggested above or install a larger capacity tank. I have a 30 gallon which I run at 160* and then mix down. Our family could take 6 showers in a row, with both baths going simutaneously on Sunday morning getting ready for church and not run out.
Bottom line. Nail your actual heat loss down and size the boiler as close to that as you can. Installing a heating plant without a good heat loss is like driving from New York to LA without a map. You'll probably get there either way, but it's a lot better with the map.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements