Pressure activated bypass
heat zone hammer
Installed hot water baseboard heating system with four zones and on one zone when t-stadt is satisfied and zone valve closes there is some hammering. Never ran into this problem before on the many installations I have done. I have tried a few things to cure the problem and they haven't work. I am baffled. Can someone please lead me in the right direction?0 -
Hammer
What type of zone valves, etc... Honeywells can hammer sometimes, also may be relay noise on boiler,, Burnham RV's mount the relay on a panel, and the relay can vibrate the panel,,anyone will need more info on the system to help you out0 -
heat zone hammer
Heating system was installed in two story modular home so baseboard and kickspace heaters already installed. Installed a Peerless WBV-04 oil fired boiler. There are four zones. One for 2nd floor, two for 1st floor, and one for 50gal indirect water heater. All zones have Honeywell V80436-1012 3/4" zone valves on supply header ( 1-1/4 ). Return header is 1-1/4 and has a Taco 007 circ. The relay box is a Taco for four zones w/priority. The zone that hammers is on the 1st floor and is furthest away from boiler and is approx (from supply to return)100'.0 -
Pull one of
the return springs off the zone valve it will close slower0 -
Bruce. Thanks for your suggestion. I guess you have run into this before. Have you found it to be common with Honeywell zone valves? I use them all the time and this is a first for me. I will try your suggestion on the job this week.0 -
Pressure activated bypass0 -
Sorry it's an O.C.D.0 -
Try Taco heat motor type zonevalves
To eliminate the water hammer from the fast acting spring loaded valves. The Taco 570 series zone valve closes slowly to prevent, or at least minimize the water hammer. For your reference I have attached the catalog data information. For additional assistance visit www.taco-hvac.com
Joe Mattiello
Technical Support Technician
Tel. 401-942-8000 X 484
Fax. 401-942-2360
1160 Cranston St
Cranston, RI 02920
joemat@taco-hvac.com0 -
Verify the direction of flow. The valves will be noisy if not correct.0
- 86.3K THE MAIN WALL