heat loss

Brad White_9
Brad White_9 Member Posts: 2,440
Not sure of the insulation that may be applied to the inside ("the outside log look") but assuming it is a conventional log cabin I take the core wood thickness as a constant. Forget the "bumps", just the common thickness within each log.

Say you have 8-inch logs and a core thickness of 4 inches of softwood (R=1.25 per inch for a material transmission of 5.0). Plus your indoor and outdoor air films (0.68 and 0.17 respectively). Total R would be 5.85.

"u" factor would be 0.171 for the wall assembly.

Comments

  • Damien Bamberg
    Damien Bamberg Member Posts: 1
    heat loss question

    I'm a sales/purchasing agent @ a Plumbing warehouse, and i'm doing a heat loss for a customer. My problem is that the heat loss is for a new log cabin in northern Maine. I don't know the proper r value or the right figs. to use

    Any one that can help me with this ? would be much app.

    thank you for your time
    Damien