Not sure of the insulation that may be applied to the inside ("the outside log look") but assuming it is a conventional log cabin I take the core wood thickness as a constant. Forget the "bumps", just the common thickness within each log.
Say you have 8-inch logs and a core thickness of 4 inches of softwood (R=1.25 per inch for a material transmission of 5.0). Plus your indoor and outdoor air films (0.68 and 0.17 respectively). Total R would be 5.85.
"u" factor would be 0.171 for the wall assembly.
Say you have 8-inch logs and a core thickness of 4 inches of softwood (R=1.25 per inch for a material transmission of 5.0). Plus your indoor and outdoor air films (0.68 and 0.17 respectively). Total R would be 5.85.
"u" factor would be 0.171 for the wall assembly.
0
Comments
-
heat loss question
I'm a sales/purchasing agent @ a Plumbing warehouse, and i'm doing a heat loss for a customer. My problem is that the heat loss is for a new log cabin in northern Maine. I don't know the proper r value or the right figs. to use
Any one that can help me with this ? would be much app.
thank you for your time
Damien0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements