f09 fault on a Munchkin80
Guy_6
Member Posts: 450
Flow Gradient Limit is something that I saw on nearly every boiler that I worked on and it is nothing. Essentially it appears when the supply and return delta is higher than the control expects. On a cold start, that is nearly every cycle. This has nothing to do with the F09.
The F09 could stem from low gas pressure, lean gas mixture, or condensate issues as listed above. Check the flame current with the software. It should never fall below 1.0 at any point. 2.0 to 4.0+ is the normal range.
If it is falling below, the usual cause is the gas/air mixture. Check the CO or CO2 levels out the vent.
Keep HTP in the loop with this- they want to help.
The F09 could stem from low gas pressure, lean gas mixture, or condensate issues as listed above. Check the flame current with the software. It should never fall below 1.0 at any point. 2.0 to 4.0+ is the normal range.
If it is falling below, the usual cause is the gas/air mixture. Check the CO or CO2 levels out the vent.
Keep HTP in the loop with this- they want to help.
0
Comments
-
Munchkin fails with F09
I contunue to have problems with my Munchkin boiler I have acces to the HTP925serv software and it is reporting F09 No ignition with the blocking Flow Gradient limit. Any ideas0 -
clean flame sensor0 -
What's the flame signal read?
the digital readout and/ or that software will tell you.
How long has it been installed? Was it set up with a combustion analyzer? What were the hi and low fire readings? I like to record them in the owners manual or on the boiler jacket itself.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Check Condensate
Have you checked to be sure the condensate drain is clear? We had a 140M intermittantly tripping on flame failure recently. Condensate was draining but not at the rate the Munchie was producing it during longer firing cycles.
Larry0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements