Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Steam/HW system setback - Energy Savings
Steve Garson_2
Member Posts: 712
My understanding is a 1* set-back for 8-hours will save 3% for those 8-hours. So if you look at 24-hours, that 3% savings is really 1% of the day's fuel consumption.
So a 9* set-back would save 9%. But you need to be sure that the system can bring the building up to normal temp in time for business hours.
So a 9* set-back would save 9%. But you need to be sure that the system can bring the building up to normal temp in time for business hours.
Steve from Denver, CO
0
Comments
-
Steam system savings with night setback
Hi,
I work for a district energy supply company. We have a customer who is installing DDC controls in a commercial building.
He runs the steam through a heat exchangeer and then hot water is used for heating througout the building.
He will be replacing the controls since the old pneumatics are shot, but the accounting dept wants to get an idea of the number of years payback this project will be. He plans on using a night setback control to lower the water set point from 180 degF to 90 degF for 9 hours overnight (8pm-5am).
I know there are other savings possibilities, but for this portion, is there a rule of thumb for the % of energy saved? I can then take that percentage and plug it into his historical data and determine a monetary savings for him.
Thank you.
0 -
I'd plan very carefully to make sure you can recover your water temp in the time you're allowing. I'm not saying you can't---it's just that you want to make sure. Too cold water isn't worth energy savings.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements