Amp rating for 24V stats.....boilerpro

superMARKet
superMARKet Member Posts: 87
http://customer.honeywell.com/Techlit/Pdf/68-0000s/68-0280.pdf (page 2)

Comments

  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    ? especially on Honeywell stats.

    I have noticed that many of the new electronic stats do not have a published amp rating for switching. I recently installed a vision pro and could not find it in the literature and Honeywells' site doesn't seem to be of much use.....at least I can't find it. In this case, the stat was controlling a Weil Mclain LGB directly, which has a pretty heavy amp load. I have another application where the draw is also high and would like to know the ratings. Can anyone point me to where this info can be found. Otherwise, I may have to install isolating relays on most steam applications because,if using an anticipator stat, you cannot achieve a one cycle per hour operation,if needed.

    Boilerpro
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    Thanks, but

    I can't seem to get the page, maybe I'll try again later.
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    Thanks, but

    I can't seem to get the page, maybe I'll try again later.
  • Glenn Harrison_2
    Glenn Harrison_2 Member Posts: 845
    BP,

    If you did a copy and paste of the link, did you copy the end where it says (Page 2)? If so copy and paste the link but stop the copy at the end of .pdf I opened the link about 10 minutes before you posted and it worked fine for me. The only other thing I can suggest is do you have the latest version of Adobe Acrobat Reader (7.0.5)?

  • ChasMan
    ChasMan Member Posts: 462


    It says .02 - 1.0 amps. Not very much.. can probably barely run a zone valve.
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    DUH!!!

    Looks like I need to go back and put in an isolation relay. Only 1 amp is pretty wimpy, a T87 can do more than that.

    Boilerpro