Correct main vents for steam system
Steamhead
Member Posts: 17,387
fron the beginning to the end of a single steam main? That's a lot of pipe. What diameter is it? Once you have this, the volume of air can be calculated, and the results tell you the main vent capacity needed.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
0
Comments
-
Correct main vents for steam system
I just joined the facility committee of a neighborhood club heated with One-pipe steam. The building was built in 1918 and the are fresh air vents that have radiators, which I had only seen in Dan's book.
The steam mains run around 150 feet, running in a "U-shape" around the perimeter of the building. I searched all over the basement and first floor for main vents and couldn't find a single one. The boiler is only four years old so I wonder if the installer removed them and never replaced them. Sounds crazy.
Anyway, what size vents would I need to install at the end of the main run to effectively vent this system?0 -
correct main vents
would this be in the magus club in wellesley?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
It's the Windsor Club in Waban, Ed.
The main starts off as what appears to be a 4-inch pipe and then gets smaller at the end. It's wrapped in asbestos, so I can't tell you what the smaller size is or when it changes down.
After calculating the volume of air in the pipe run, what is the formula to determine the correct vent size? I never saw anything of the sort in Dan's books about steam.
Steve0 -
Balancing steam systems using a venting capacity chart
There is an e-booklet on sale here that explains how to empirically come up with the good venting scheme.
Essentially you start by installing vents one by one. Each time you measure the time it takes your system to heat up at the radiators. When the addition of one more vent shows no decrease in heat up time, you know you've reached good venting.
The booklet is by Gerry Gill and Steve Pajek.
With steam heat, the Windsor Club must be a swanky place to be a member of. Good thing they've got you on the building committee.
0 -
Actually, the club isn't real swanky. All the neighbors back at the turn of the century took out a loan and built a club house and two tennis courts. Today, it's still for neighbors, but now has four courts, a pool, and three bowling lanes in the basement. I've got all summer to get the steam system working properly.0 -
Have a wonderful summer
Steam heat makes your club swanky for me...
Christian0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements