Insulating with Subfloor Radiant tubing
it's personal preference in the regard that it doesn't matter much. it's not needed though.
0
Comments
-
Difference of Opinions
when it comes to Installing Fiberglass insulation between floorjoists... after tubing, WITH heat transfer plates, and possibly radiant barrier/foil. SOME people insist that there should be a 1 1/2inch to 2 inch airspace between the insulation and tubing/plates... where others .. including the Wirsbo Instal Handbook... shows NO airspace with this instal method.. unless youre doing a suspended tubing instalation method... then yeah.. you're heating the AIRSPACE which heats the floor... needs the gap between the batting and flooring... thats a given... BUT... is this another personal preference? or equally effective methods varying from one Radiant manufacturer to another?
Thanks again
Russ0 -
With floor plates,
you're heating by conduction and an air space is not necessary. So, to answer your question it's not a personal preference; it's physics.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
bad news, good news
Russ,
The bad news is that you are talking about pink stuff. It's my least favorite insulation material. The good news is that insulating the joist bays on a subfloor transfer plate install is the best possible case for pink.
The problem with pink is that it does not resist air motion very well, so convective currents can set up greatly reduce the insulation value. The good news is that a subfloor joist space with top surface heat is the most stable air pattern to be found in a house, so the pink penalty will be less. I would use a better insualtion than pink near the rim joists, as that is the greatest loss area and the air is less stable there.
There is no purpose for the space in a transfer plate installation. Leaving the space makes it harder to get the tightest possible fit for the insulation, which is always the goal. So I would fill it up and make sure it is installed with as close to zero voids (small uninsulated sections) as possible.
hope that helped
jerry
0 -
I second the reservation about fiberglas
whether it is pink or yello. A far better product in every case is called Roxul which you can get at HD. This stuff is a byproduct of some kind of mineral smelting. It is green in color and in its environmental impact. It is also much more benign to work with.
Keep the air spaces to a minimum, as already stated by those with practical experience. Don't lose sleep over the inevitable small voids where plumbing and electrical services interfere with a perfect insulation installation.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 939 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements