T8400B T Stat
Empire_2
Member Posts: 2,343
You may want to check the va rating on the t-former powering these t-stats and also chect to see if there is any voltage drop. What is the actual voltage on the t-stats when not calling for heat? Are the Stat lines excessivly long?
0
Comments
-
Carol
The 8400 power stealing T Stat, been having issues with displays going blank at intermitent times.
6 T Stats in all, wired to simple 6 zone controller, customer just called to inform me that when he turned one T Stat on, all 6 went blank. This isn't the first time this has happened, eventually they seem to reset themselves and work fine, curious if you have any insight to this problem. Thanks0 -
Haven't heard of this before and I'll see what the engineer says. In the meantime, let's remember that a thermostat isn't a load and has a very small amp draw. As I remember, these stats do 80 milliamps. Of course, each controls a load that does have an amp draw. I'm on vacation, for the rest of this week, so expect to hear from me next week.0
This discussion has been closed.
Categories
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 768 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
- 17 Recall Announcements