pump question?

RoosterBoy
RoosterBoy Member Posts: 459
hay guys on one side of my house i have a baseboard loop with a taco 007 i am installing a new zone 55ft of suntemp basebord on the other side of my house this week and want to use a grundfos 1558 on speed 2

will running the 1558 at a lower speed at the same time as the 007 be Okay. or will i have problems.

will lower speed be better for heating then at speed 3 like a 007 id like to move the other zone to a 1558 also

thank you

Comments

  • RoosterBoy
    RoosterBoy Member Posts: 459


    anyone? :-)please help
  • Bob Sweet
    Bob Sweet Member Posts: 540
    Rooster Boy

    are you running this set up pri/sec ?
  • RoosterBoy
    RoosterBoy Member Posts: 459


    no im not doing primary secondary looping i thought that was just for radiant floor

    sometimes both zones will come on at the same time right now i use hydro air on this side of the house and baseboard on the other now i am installing baseboard to replace the hydro air and just keep the duct for my ac last year i used 2 007 and it worked fine im just not sure if running 2 pumps at different speeds is okay

    my setup is a g115 with riello burner lt 160 dhw tank and r2107 buderus outdoor reset

    thanks



  • hr
    hr Member Posts: 6,106
    You need to know

    how many btus are needed and the pressure drop to accuratly answer that question. Add up all the baseboard lengths, and the copper piping and fittings and do some calculating. A rule of thumb is not more than 67 to 70 feet of 3/4" baseboard on a zone.

    It may be best to add a second zone and circ pump if your lengths are getting out there.

    The free Slant Fin calculator, on this site would answer a lot of the questions :)


    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Bob Sweet
    Bob Sweet Member Posts: 540
    pri/sec works well

    with any set up (rfh, BB, HA ), it allows pumps to work independantly or in tandem regardless of what each pump is doing, along with a bit of boiler protection from return temps. My guess is if the heat load hasn't changed youll be fine.
  • RoosterBoy
    RoosterBoy Member Posts: 459


    OK i'm not sure how to calculate the pressure drop and gal per min flow. but maybe this will help the whole loop is being piped in pex and will total 138 feet that includes 55ft of baseboard loaded for 170deg on -8 deg day in connecticut

    thanks
  • RoosterBoy
    RoosterBoy Member Posts: 459


    ok i added up the btu in each zone and came up with this
    BTU divided by 10,000

    zone 1 gave me 2.4gpm flow and zone 2 gave my 2.9gpm flow
    not sure how to do pressure drop

    i was thinking of piping this zone with a home run setup and still use just one t-stat this way here i wont need a differential pressure bypass valve because all baseboards would run at the same time every time there's a call for heat it's a small part of the house with 2 bedrooms it would be crazy to run t stats in every room :-)
  • RoosterBoy
    RoosterBoy Member Posts: 459


  • thp_8
    thp_8 Member Posts: 122
    007

    I hate to muddy the waters, but I will. Your first 007 is more than enough circ. for the whole job. If it was mine, I would zone valve the set up and just use the one circ. Always looking to use the least amount of power. Total energy effiiency is often overlooked.
  • RoosterBoy
    RoosterBoy Member Posts: 459


    thanks thp

    zone one has 47 feet of baseboard and is a 120ft loop that includs the 47 ft of basebord

    zone 2 will be 55 ft of basebord and i want to do it as a home run so each room gets 170deg

    thanks