pump question?
 
            
                
                    RoosterBoy                
                
                    Member Posts: 459                
            
                        
            
                    hay guys on one side of my house i have a baseboard loop with a taco 007 i am installing a new zone 55ft of suntemp basebord on the other side of my house this week and want to use a grundfos 1558 on speed 2
will running the 1558 at a lower speed at the same time as the 007 be Okay. or will i have problems.
will lower speed be better for heating then at speed 3 like a 007 id like to move the other zone to a 1558 also
thank you
                will running the 1558 at a lower speed at the same time as the 007 be Okay. or will i have problems.
will lower speed be better for heating then at speed 3 like a 007 id like to move the other zone to a 1558 also
thank you
0                
            Comments
- 
            
 anyone? :-)please help0
- 
            Rooster Boy
 are you running this set up pri/sec ?0
- 
            
 no im not doing primary secondary looping i thought that was just for radiant floor
 sometimes both zones will come on at the same time right now i use hydro air on this side of the house and baseboard on the other now i am installing baseboard to replace the hydro air and just keep the duct for my ac last year i used 2 007 and it worked fine im just not sure if running 2 pumps at different speeds is okay
 my setup is a g115 with riello burner lt 160 dhw tank and r2107 buderus outdoor reset
 thanks
 0
- 
            You need to know
 how many btus are needed and the pressure drop to accuratly answer that question. Add up all the baseboard lengths, and the copper piping and fittings and do some calculating. A rule of thumb is not more than 67 to 70 feet of 3/4" baseboard on a zone.
 It may be best to add a second zone and circ pump if your lengths are getting out there.
 The free Slant Fin calculator, on this site would answer a lot of the questions 
 hot rod
 To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
- 
            pri/sec works well
 with any set up (rfh, BB, HA ), it allows pumps to work independantly or in tandem regardless of what each pump is doing, along with a bit of boiler protection from return temps. My guess is if the heat load hasn't changed youll be fine.0
- 
            
 OK i'm not sure how to calculate the pressure drop and gal per min flow. but maybe this will help the whole loop is being piped in pex and will total 138 feet that includes 55ft of baseboard loaded for 170deg on -8 deg day in connecticut
 thanks0
- 
            
 ok i added up the btu in each zone and came up with this
 BTU divided by 10,000
 zone 1 gave me 2.4gpm flow and zone 2 gave my 2.9gpm flow
 not sure how to do pressure drop
 i was thinking of piping this zone with a home run setup and still use just one t-stat this way here i wont need a differential pressure bypass valve because all baseboards would run at the same time every time there's a call for heat it's a small part of the house with 2 bedrooms it would be crazy to run t stats in every room :-)0
- 
            
 0
- 
            007
 I hate to muddy the waters, but I will. Your first 007 is more than enough circ. for the whole job. If it was mine, I would zone valve the set up and just use the one circ. Always looking to use the least amount of power. Total energy effiiency is often overlooked.0
- 
            
 thanks thp
 zone one has 47 feet of baseboard and is a 120ft loop that includs the 47 ft of basebord
 zone 2 will be 55 ft of basebord and i want to do it as a home run so each room gets 170deg
 thanks
 0
This discussion has been closed.
            Categories
- All Categories
- 87.2K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 427 Carbon Monoxide Awareness
- 118 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.7K Gas Heating
- 112 Geothermal
- 164 Indoor-Air Quality
- 3.7K Oil Heating
- 73 Pipe Deterioration
- 1K Plumbing
- 6.4K Radiant Heating
- 393 Solar
- 15.5K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 49 Job Opportunities
- 18 Recall Announcements