thermistor sensor

kevin coppinger_4
Member Posts: 2,124
ever used a thermistor sensor to measure the water temp of a buffer tank or indirect water heater w/o the use of a sensor well....surface munt on steel and insulated well on top? ty, kpc
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=323&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
Sure
all the time. I'd use some thermal grease.
Be sure the sensor is held tightly against the tank. And yes, insulate over the sensor.
When I use electric water heater tanks I slide the sensor under those metal clips that hold the upper and lower thermostats in place. This puts a good tension on the sensor and the element insulation blanket covers all.
Another method is to use a stainless hose clamp and fasten it to the pipe as it exists the tank. Then some Thermacell insulation. If you want the sensor at the very top of the tank.
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements