sidewalk heating

Fred Polski
Fred Polski Member Posts: 1
My goal is to heat a sidewalk when it snows or when we get freezing rain. It would not be used all the time,,,only when inclement weather strikes.
I recently poured a concrete sidewalk containing about 350 ft. of 1/2" pvc tubing. The tubing is snaked throughout and is about 2" beneath sidewalk surface. Total sidewalk space is about 400 sq. ft. Could I use an electric 20 gallon hot water heater to heat a glycol solution and then pump it into the walkway?

Comments

  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    pvc tube???

    for starters...you have got to do a heatloss...unless you do that you are guessing. Did you insulate? you don't know if you even have enough tube to make it work, hopefully so...snowmelt requies a lot of engrgy fast....get the #'s done then you know.kpc

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Singh_3
    Singh_3 Member Posts: 58


    1/2 pvc tubing or 1/2 pex tubing? big difference.
  • mikea23
    mikea23 Member Posts: 224


    PVC or pex it doesnt much mater 400Sq on one loop of 1/2. With a loop lenght of 350 feet thats about 12" spacing get the jack hammer
  • hr
    hr Member Posts: 6,106
    depends on your expectations

    I plan on at least 100 btus per square foot, or in your case a 40,000 BTU load. You would need a dual element tank with two 6 KW elements to get there. 12KW X 3.41= 40,920.

    The tube spacing is a bit wide and the diameter a bit small for that space, but it would do some melting, slowly :)

    PVC wouldn't be my first choice, but I have actually seen PVC on hot water baseboard systems!

    PVC is not a very glycol friendly product however :( When I did CPVC fire sprink systems we had to use glycerin as the antifreeze. Glycols will go after PVC.

    My neighbor in Utah, the Vanguard rep :) had a 50 gallon 40K input gas fired WH driving some 1/2" PB in about 800 square feet of drive. I'm amazed at how well it actually worked. Slow, but it always got the job done.

    hot rod

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • steven e heat
    steven e heat Member Posts: 2
    please tell me no!!

    please tell me you have several loops of 12 " tube. otherwise your lookin@ bout 100' of head.