Modine on a 1 pipe steam system ?
to heat part of a warehouse / showroom . The place has a liitle of everything - warm air , hot water heat and steam .
The room in question had a few steam rads that were removed and capped . For some reason the customer does not want rads . I'm guessing they need the wall space ( I haven't seen the place yet ) .
One option is a hanging modine driven by steam . There is a 1 1/2 inch steam riser very close to where we can hang the unit . The caveat is no real easy way to run a separate return pipe if needed .
Anyone have any luck using a Modine with 1 pipe steam ? Any piping ideas you can share ? Thanks in advance .
The room in question had a few steam rads that were removed and capped . For some reason the customer does not want rads . I'm guessing they need the wall space ( I haven't seen the place yet ) .
One option is a hanging modine driven by steam . There is a 1 1/2 inch steam riser very close to where we can hang the unit . The caveat is no real easy way to run a separate return pipe if needed .
Anyone have any luck using a Modine with 1 pipe steam ? Any piping ideas you can share ? Thanks in advance .
0
Comments
-
mod. valve
Did a few in the early seventies using modulating valves0 -
You need a return from the UH
but it doesn't have to go back to the wet return. Somewhere I have a piping diagram of this hookup- I'll see if I can find it.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
I know it's in one of Dan's books with a radiator. If the pipe is large enough for the unit heater it should work as well. Drop the return low and make a loop seal and then connect it to the riser.
ED0 -
Thank you all for the advice
Before I could check in with you gents , they sprung the job on us . We lucked out big time with a wet return in the basement that was real close . We used an F and T trap and the Modine worked flawlessly . Actually it worked too good . We'll probably be back to throw a thermostat on the unit .
Thanks again guys .0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements