Pumped system
William Faust
Member Posts: 168
My 2-pipe steam system is pumped. The only vent is an open pipe at the boiler feeder. I was planning on installing main vents to speed the purging of air from the mains. Am I on the right track here or is this done only for gravity-return systems?
0
Comments
-
The receiver tank
mainly handles air from the dry returns, which mostly comes from the radiation. Some air passes thru the F&T traps on the steam mains but this is typically not enough for good venting. Vent your steam mains and watch the difference.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Thanks for confirming
my understanding.0