Are my main vents broken shut?

Daniel_3
Daniel_3 Member Posts: 543
Who knows how old they are but I have two main vents at the and of my dry returns. One is a Dole 3B and the other is an Amtrol float type with a small screw cap on top (seems to be for a hydronic system since inside the screw cap there is a pin which depresses). Well after trying to blow through them there is no flow. I know this, that normal 1/8" rad vents should let air through yet it seems these don't let anything through so I'm thinking because they are fused shut permanently that's why it takes about 1 1/2 hours of burn time to get from 60^ to 65^ in the morning because the mains are not being properly vented. I'm already looking for new main vents as I type this. One piper steam with about 2,500 sqft. of living space. The mains are about 34 ft. and 39 ft. a piece and dry returns are about 35 ft. a piece.

Comments

  • Big Ed
    Big Ed Member Posts: 1,117
    Main Vents

    1/8 tappings are too small for main vents. Should be repiped to a 3/4 tap. In the mean time use a Verivent from Heat timer. Very fast venting.

    Improper venting would efect the balance.
  • William Faust
    William Faust Member Posts: 168
    why a larger tap?

    I assume that there would be no need to repipe the tap from 1/8" to 3/4" if the Heat-Timer VARIVALVE could vent air as fast as needed. Do I understand this correctly?
  • Daniel_3
    Daniel_3 Member Posts: 543


    The first vent from Amtrol is definitely a hot water vent. The Dole does flow air but slowly and with some strange sound as if it has some blockage. I am planning on getting some hoffman 75's so I'll deal until then.
  • Daniel_3
    Daniel_3 Member Posts: 543


    The Dole 3b is a 1/4" tapping
  • Daniel_3
    Daniel_3 Member Posts: 543


    I just noticed something in "The Lost Art" after considering the venting of the dry returns at the boiler area. Why should I spend the time venting the massive amount of air on the 33ft. long dry returns when I could tap and pipe up 15 inches two main vents at tht end of the main on the other side of the basement?
  • Steamhead (in transit)
    Steamhead (in transit) Member Posts: 6,688
    You're absolutely right

    and if you're using Hoffman vents, I'd use two #75s on each main with a #4A added to the longer one alongside the two #75 vents. You could also use two Gorton #1 vents on each main along with the Hoffman #4A on the longer one.

    To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"
  • Daniel_3
    Daniel_3 Member Posts: 543


    That's exactly what I'll do Steamy. Thanks!