air in system

Ragu_5
Ragu_5 Member Posts: 315
That is a new one on me; thanks! You are a good teacher.

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=428&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Bill_88
    Bill_88 Member Posts: 2
    air in system

    This is a repeat of a question I asked two days ago "air vent". Can a faulty air vent allow air into a radiant floor heating system. If there is no leak what ways could air be getting in. Tubing is high quality Stadler cross linked pex. System had worked flawlessly for 14 years. Now lots of air in lines but steady 12 psi pressure. Could anyone point me in the right direction. Thanks
  • Ken_40
    Ken_40 Member Posts: 1,320
    The real question is:

    Is the vent loacted properly? If so, it CANNOT let air into the system. If in the wrong location, it will allow air in and it is not a faulty vent, rather a faulty circulator!

    Either a wrongly placed circulator is creating a vacuum at the vent piping area, or a new circulator with higher head is creating a vaccum where not used to exist.

  • Big Ed_3
    Big Ed_3 Member Posts: 170
    Air Problem , Somthing to Look For

    Which type expansion tank is being used ? Diaphragm type ? Is it sticking up rather then hanging down ? Where and how is it connected to the boiler ? Sometimes the bladder tank will loose its charge and if it is sticking up it will act like a air trap . It would collect and release air on pressure change. Would drive you nuts.
  • Clyde Edmonds
    Clyde Edmonds Member Posts: 9
    air in lines

    Under the supervision of my heating supplier I installed my in floor heat system about 11 years ago. It has worked perfectly until last season when air began to accumulate in the lines. I can purge the air from the system but it returns in a couple of months. Could a faulty expansion tank cause this? It is installed hanging down. Is this correct?
  • Clyde Edmonds
    Clyde Edmonds Member Posts: 9
    air vent

    Can you describe an "air vent". I installed my own system several years ago but have recently been getting a buildup of air in the lines causing a lack of hot water delivered to the floor.
    Thanks
  • Brad White_184
    Brad White_184 Member Posts: 135
    Clyde

    You may want to post your posts together into a single "New Thread" to get the attention it deserves. Yours are tagged on to an older thread, albeit of similar topic, but you can get more specific answers to your needs.