garvity vs forced hot water heating

Jim_109
Member Posts: 45
As a homeowner how can I tell if I have a gravity or forced heating sytem? I have cast iron baseboards and radiators on the first floor and slant fin basboards on the second floor.
I am considering purchasing a new boiler and indirect, as well as possibly adding a full bath to the second floor. Currently I have only have one bathroom on the main floor.
How much does it matter which type of heating, forced or gravity when considering a new boiler and indirect.
Also any comments about pressure boosters? I have low water pressure in the kitchen and bathroom. The water company says the pressure is on the low side, but "normal"
I would like to increase the pressure to the fixtures, plus I am concerned about the low pressure if I add the full bath to the second floor.
THANKS!!! Jim
I am considering purchasing a new boiler and indirect, as well as possibly adding a full bath to the second floor. Currently I have only have one bathroom on the main floor.
How much does it matter which type of heating, forced or gravity when considering a new boiler and indirect.
Also any comments about pressure boosters? I have low water pressure in the kitchen and bathroom. The water company says the pressure is on the low side, but "normal"
I would like to increase the pressure to the fixtures, plus I am concerned about the low pressure if I add the full bath to the second floor.
THANKS!!! Jim
0
Comments
-
Jim, go to the boiler
and look for a circulator. I suspect you have one. Gravity via fin-tube coupled with cast iron sounds a little odd to me. At least the upper floors have more pressure differential which can help.
Now, noting that you have cast iron and fin-tube, I would hope that if you go to a positively circulated system that you separate them. Keep cast iron together on one zone, fin-tube or any low mass emitters on a separate zone.
As for pressure boosting, 80 psig is code maximum in most places. 40 psig is considered a minimum. What is the actual number under a flow condition? Watts and others make a gauge that fits on a hose-end connection. To be fair, take a reading when there is flow in the system, not just a static reading with no flow. That will be an unfairly high pressure, not indicative of much.0
This discussion has been closed.
Categories
- All Categories
- 84.3K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 44 Chimneys & Flues
- 1.8K Domestic Hot Water
- 4.8K Gas Heating
- 120 Geothermal
- 156 Indoor-Air Quality
- 3K Oil Heating
- 57 Pipe Deterioration
- 794 Plumbing
- 5.4K Radiant Heating
- 370 Solar
- 14.1K Strictly Steam
- 3.1K Thermostats and Controls
- 54 Water Quality
- 39 Industry Classes
- 80 Job Opportunities
- 22 Recall Announcements