Oil Burner Failures

Ed Jesteadt
Member Posts: 1
I have a slant fin L30P burner that has failed 3 times in the past 8 years - seems to burn dirty - clogs up - shuts down - properly maintained. Are these systems defective? Anyone else have problems with these systems
0
Comments
-
Where is it "clogging up", exactly? What service is needed to remedy? What are the combustion readings? Please give more details on the oil supply system - tank location and age, supply piping, etc...0 -
Don't
complain. 3 service calls in 8 years is way below average
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
I'm with Lurkin. More info please.
Oil lines clogging = Are your filters adequate size for your usage and are they changed regularly? Quality of the oil tank, etc,..
Flues clogging = Adequate combustion air to the boiler room?Dryer lint clogging the burner fan? Proper combustion testing and setup?
There are so many different things it could be. More info would be helpfull.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional""We see the world as WE are, not as IT is, because it is the "I" behind the EYE that does the seeing"0
This discussion has been closed.
Categories
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 768 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
- 17 Recall Announcements