Noritz wall hung hot water
john_83
Member Posts: 76
Wondering if anyone has had problem with fintubes in unit freezing up . Had one freeze up and burst the unit has automatic damper and heater to prevent people from noritz cant figure it out. never lost power thanx john
0
Comments
-
coil freeze
Check the building for depressurization: even with a damper, it can leak enough to freeze under the right conditions. ie: make-up air screen plugged, exhaust systems left running overnite, etc. etc.0