Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

One pipe steam system main relief

Mad Dog_2
Mad Dog_2 Member Posts: 7,518
and get a heating pro in there....any pro for now. It sounds like you could have a blocked pigtail or non-working pressuretrol - THIS IS VERY DANGEROUS! THat's more than 15 pounds of steam exiting that valve. Keep family and pets out of basement until it is corrected. Mad Dog

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=210&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Al_23
    Al_23 Member Posts: 4
    Steam system one pipe

    The main relief on the furance keeps lifting filling the basement with steam. The raditor vents all seem to be working reliving the pressure/steam This has never happen before Boiler is probably 40 years old Its a one pipe steam system I have replaced 4 of the 8 vents on the raditors
  • Al_23
    Al_23 Member Posts: 4
    Pigtail /pressuretrol

    Thanks mad Dog you hit the nail on the head It was a clogged pigtail I had the Gas company come do it took about 15 minutes and it was all fixed next time will do it myself
    Thanks again
This discussion has been closed.