How to convert standing pilot to elctronic ignitor?

is in that boiler? Can you post some pics? Also, what is the Input rating of the burner?

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>

Comments

  • Kitchenman
    Kitchenman Member Posts: 3
    Conversion of standing pilot to electronic ignition on old boile

    First thanks to Dan I have learned more about steam systems than some of the pros from your books.I hav 1970 Kewanne boiler, I have had it retubed and don't hav $ for a new unit
    I would lik to get rid of the standing pilot & replace it with a Ignition transformer & elec.spark ignitor.Every pro has told me it's not made.Tell me their wrong.The main to the gas valve is 1 1/4 honeywell V48a.If there is a pro in chicago that can do this email me.
  • Why would you want

    to convert it over to EI? It is very possible with that V48 application you are running at pretty high BTU input so I would not suggest doing that conversion as you may be asking for problems with good flame proving. The alternative would be a Flame Safeguard Commercial application which would be very costly and would need boiler company approval for such a design change.
  • WHat Tim said....

    You're about to bite off a chunk of liability that your homeowners insurance probably won't approve should there be an issue...