vacuum condensate return
Options

dom bencivenga
Member Posts: 1
I have a jennings "vacuum heating pump' which has 2 condensate pumps and 2 hurling pumps. The system will not make a vacuum. Any help is greatly appreciated. The system worked great for the last 60 years.dom..
0
Comments
-
won't make vacuum
Assuming that the pump and controls operate, what is the return temperature as it enters the tank?
Noel0 -
1-Does the tank have enough water for the (hurling) air pumps?
2- Are return lines leaking? Sucking sound if air pumps work and water leakage when air pumps are off.0 -
Check seals
and water level as noted. After 60 years, everyone has a leak problem it is written... I saw one years ago with a nice neat hole between the hurling tank and the main tank, just rotted out in a spot for reasons unknown but it was a steel tank, not CI. Can you check tank integrity?0