It is suggested to use the domestic hot water tapings on the GB142 manifold and the domestic hot feature we offer. If the DHW priority is used on the GB142, the boiler will fire to high limit (194 degrees F), de-energize the primary loop pump and ignore the delta T modulation. When the domestic is treated like a zone of heat (priority zone on a relay board) the GB142 does not reconize it as a call for domestic hot water and will modulate the burner based on the delta T, just like a heat zone. This could cause the domestic to take longer to recover. The use of a "kick space" type of heater should not be an issue. Please contact me if there are any questions.
0
Comments
-
piping question with gb142
i just had all new piping installed with my existing boiler
can the indirect use the existing piping or does it need to piped thru the manifold sent with the boiler. also i have toe kicks on one zone and cast iron radiators in remander of house. any problem with the toe kicks using the 142 with modulation0 -
GB
Hey Mark,
You should pipe the domestic tank to the provided taps on the provided manifold. Reason being is that the provided boiler pump shuts off on a call for domestic. You must also upsize your domestic pump to overcome the high resistance in the boiler.
If the boiler came with the AM10 reset control you would want to program it for the highest temp heat emitter.(The toad space heater) The dial on the boiler should be set for AUT
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements