I heve a weil McLain 368st with a beckett afg burner on it. It was serviced last week,The stack temp gross was 420/ net350, co2/ was 11.3,draftBr/.04, of .02smk,0/ co100/, are these # good ? thanks tom

Comments

  • Ken_40
    Ken_40 Member Posts: 1,320
    They are...

    On the money!

    Whoever did the work should be kept.

    Believe it or not, most guys don't leave the combustion tags on their work. Some, because they didn't do it; others, because they did it, but don't know why.
  • Big Ed
    Big Ed Member Posts: 1,117
    One Small Adjustment

    I would give up some of that CO2 for a lower CO.. Why not Zero.

    Also what is the draft over the fire.. Weil McLanes are a little tight.
  • tom_11
    tom_11 Member Posts: 58
    # after service

    How low should the co2 be , the over fire # are 02, also how about the 02. Thanks tom
  • Big Ed
    Big Ed Member Posts: 1,117
    CO2

    What the manufacture design. Should be posted on the boiler.Most pin type boiler require -.02.. All boilers are different.Some boiler are designed to run + pressure.

    The CO2 max on oil should be 13 percent,but on this state the boiler is running like a hot rod.I rarely reach that that number and only on brand new equitment.You want to throttle back any way for a safey margin.Air leaks in the boilers gas seals will drop the CO2 and stack temperature..

    Accepitable CO level is 50 ppm use to be 200ppm years ago..

    The numbers as Ken mentioned are near perfect..



    PS Being a grunt for 35 years I take posted readings with a grain of salt...