New PSI Gauge
Options
Al Letellier_9
Member Posts: 929
Yes you can and the simplest way is to remove the pressuretrol and install a brass tee on the pigtail, use a short nipple and reinstall the pressuretrol. The branch of the tee should be looking at you. Use a back mount pressure gauge and install it in the branch of the tee. Make sure the pigtail has water in it before you button it up and voila.......Just a note...not my favorite place for a pressuretrol and gauge. Would rather see a tap off the boiler above the water line and a separate pigtail for each device, but you have what you have, so this will work. IF you have an old, steel pigtail, replace it with a brass one if you can.
0
Comments
-
My current pressuretrol sits alone on top of a McDowell unit.
Possible for me to add a gauge next to the pressuretrol? WHat parts do I need?0 -
gauge
Yes you can and the simplest way is to remove the pressuretrol and install a brass tee on the pigtail, use a short nipple and reinstall the pressuretrol. The branch of the tee should be looking at you. Use a back mount pressure gauge and install it in the branch of the tee. Make sure the pigtail has water in it before you button it up and voila.......Just a note...not my favorite place for a pressuretrol and gauge. Would rather see a tap of the boiler above the water line and a separate pigtail for each device, but you have what you have, so this will work. IF you have an old, steel pigtail, replace it with a brass one if you can.0
This discussion has been closed.
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 50 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements