knight won't fire
Options
[Deleted User]
Posts: 503
Inside the cover, down to the lower left, there is a white PVC cyclindrical device. THis is the condensate trap. It has a float switch inside of it that if the drain outlet plugs up, will cause this condition. You should check the drain, possibly even taking a wet vac and attaching it to the drain to make certain it is completely clear. If that doesn't work, call in the installers to have them check it out.
ME
ME
0
Comments
-
My Knight won't fire. Saying \"SW clogged drain\"..........
I can't find a clogged drain! Any ideas???????0