How much head?
hr
Member Posts: 6,106
Unless the boiler is a 55K and you are at design conditions, expect some cycling. Low mass boilers especially are prone to some short cycles when they are micro loaded.
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
hot rod
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=144&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
How much head?
0 -
How much head?
Can someone with siggy's software help me out. New boiler, seeing a temp drop of 30-35 degrees across zone 1 and boiler short cycling, wondering if circ is too small. 55K btu/hr heat loss on that zone, 1 inch copper M pipe, 150 feet long, 12 elbows, 4-45 degrees, B&G EASB-Jr air seperator, and 3 ball valves on that heating circuit with 10 cast iron rads with monoflow fittings. Currently a taco 007-ifc. I think I may have to move to a pump with higher head pressure? what do you think? Thanks Marty0 -
Short-cycling isn't reduced by increasing the flow.
If you double the flow, you have twice as much water to be heated per minute, but half the delta-T, so the boiler doesn't feel a difference.
If the boiler is short-cycling, it is probably too big. I assume only one zone is calling...it is too small for the boiler (as already pointed out above). If you can merge it with another zone, that will make a difference. The deltaT is a separate matter and 30-35F is not a problem in itself, it is fine.0 -
head question
The boiler is a buderus 115-3 section, with a riello F3 (.6 nozzle at 175 psi 0.80 gph (slightly overfired for DHW needs). Outdoor reset logamatic and usually only the one zone calling for heat (other zone is ~ 40k btu/hr heat loss). So am I hearing that a Taco 007-ifc circ is fine for that length of pipe and # of elbows? Thanks to all.0 -
Can you really have too much head?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements