Swap B&G 100 for 007
Ken_40
Member Posts: 1,320
The dynamics of both pumps are wildly different.
As long as the circulator is not mounted on the return, you'll probably be okay.
If it is on the return, you will create a monster. The monstare will be the much higher head of the 007 causing vacuum leaks where none now eist and the entire system will becom air bound at worst, make gurgling noises and have to be bled once a year at best.
If you "pump away" or re-pipe the boiler to have it "pump away" - you'll be a happy camper with the 007 or the S-100
As long as the circulator is not mounted on the return, you'll probably be okay.
If it is on the return, you will create a monster. The monstare will be the much higher head of the 007 causing vacuum leaks where none now eist and the entire system will becom air bound at worst, make gurgling noises and have to be bled once a year at best.
If you "pump away" or re-pipe the boiler to have it "pump away" - you'll be a happy camper with the 007 or the S-100
0
Comments
-
Swap B&G 100 for Taco 007
After finding circulator pump problem, think I am better off swapping the B&G for a Taco 007. The boiler is an older WM PCG-3 that came with the B&G, yet the newer ones come with the Taco. All of my heat emmiters are 3/4" copper fintube, one floor, and back to the boiler. Any suggestions why this might not be a good swap? I figure it should be a "simple" swap, flange to flange, 2 wire electric. I have never done this before, and ideas? Anything I should look-out for? I figure the 007-F5 to be the one for me?0 -
007 swap
Of course you can make the swap. On a small residental system like yours there will no problem.
Dave in DenverThere was an error rendering this rich post.
0 -
Go by flow rate and heat load
The Ubiquitous 007 may be too much pump. Know your emitters and required flow rate plus how much pipe and how many fittings to get an idea. You may do well with much less pump.
Nothing wrong with a 007 but if the circuit is a single 3/4" run 4.0 GPM (40,000 BTUH) against 9 feet of head. That is the equivalent of over 200 feet of pipe. Just a caution about over-pumping, but as others have said, it is done all the time and will work fine."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
Why not try the
Grundfoss 15-58 on low speed would probably be best if not med is close to the Taco 0070 -
Ok, now I am confused
I called a plumber friend of mine today, looking for a B&G 100, and he has worked on this boiler before. He suggested that I avoid the higher cost of replacing the B&G, by opting for the "lesser" pushing Taco 007. The boiler was installed in 1978, and I believe this is the original circulator. Another residential plumber at work suggested the Grundfos Brute (UP15-42F) saying it cost about the same as the Taco, but fits exactly in place of the B&G. Yep, my head is spinning. This is getting very deep . . . .0 -
I would follow Bruce on this one
The versatility of the Grundfos makes sense. Nothing against the 007..
If that is deep, Jimbo, we should talk sometime about the philosophy of water flow.... ouch."If you do not know the answer, say, "I do not know the answer", and you will be correct!"
-Ernie White, my Dad0 -
007
For what it's worth, to simplify this situation, remember that millions and millions of 007's have gone in to replace all kinds of other circulators. Last I knew they were all working pretty well.
The 007 won't be a problem...take my word for it.
jw0 -
It will work fine!!!
Been there, done that.0 -
And pays for itself!
0.75 amps instead of 1.75 amps
That amp difference costs $0.30 a day (assuming that it is running non-stop) or more depending on your electric rates. At $80 that's 277 days of run time. Less than 2 seasons later it's money in your pocket. It probably won't last as long as the B&G which can be rebuilt indefinitely but you can afford a new 007 with the electrical savings.0 -
Thanks . . . .
I think I will follow Bruce's advice. I was trying to go the best, yet less expenxive route. As for water flow, I got an ear full about di-electric nipples, brass ball valves, and copper pipe at work today. It seems that some folks are REALLY hung-up on installing a di-electric nipple before the ball valve. I always "thought" brass was alright, but copper was a problem. Hey, my head is still reeling . . . and now I've got to go buy a circulator and install it. Thanks for the imput.0 -
What's this indicate?
The pump I have to replace is actually blue in color, not that that matters. It "says," series 100, FU, 232. Can anyone tell me if this pump is any different than today's series 100. I'd like to swap it for a more cost-effective modern pump.0 -
same pump, different paint job
wiel-mc lain painted their series 100 blue. identical to the red ones.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements