honeywell?
Options
pipewrench
Member Posts: 3
This weekend I went to look at a down boiler that I installed 17 years ago. I probably should of sent him to the yellow pages, but hes now old and retired (I'm just old) and I thought I'd just take a look at it for him.
It a valliant, 100,000 in. its got a honeywell 586 e intermittant piolet. On a call for heat the piolet would light, no problem, but the main flame wouldnt. A little bit of wiggleing , tapping and a couple of choise words and she fired right up. An even 12 trys it failed once more.
Now he didnt have the papers from the boiler anymore. If I have anything on these controls, its buried upstaires in the barn in my "archives".
Can anyone tell me what the probale causes of this are? Could it be a simple as a dirty sensor or should I be looking at new controls.
He wants a ballpark on a hi efficent boiler, but hes got to save up for it.
Any ideas will be aprreciated.
thank you
pipewrench
It a valliant, 100,000 in. its got a honeywell 586 e intermittant piolet. On a call for heat the piolet would light, no problem, but the main flame wouldnt. A little bit of wiggleing , tapping and a couple of choise words and she fired right up. An even 12 trys it failed once more.
Now he didnt have the papers from the boiler anymore. If I have anything on these controls, its buried upstaires in the barn in my "archives".
Can anyone tell me what the probale causes of this are? Could it be a simple as a dirty sensor or should I be looking at new controls.
He wants a ballpark on a hi efficent boiler, but hes got to save up for it.
Any ideas will be aprreciated.
thank you
pipewrench
0
Comments
-
I assume you mean
a Honeywell S86E module. I have a procedure for checking that system out if you e-mail me I will send it to you for free.0 -
if its any help i have the original manual for a vaillant GA 100 boiler.... I can scan whatever section you like and e-mail if that may help0 -
It probably is an S86 spark module.
Go to www.customer.honeywell.com, look on the lower right hand corner of the screen, click on literature and type in S86 for a tech sheet to download and print out or view on screen. No charge and no password required.0 -
Thank you.....
Thank you Tim, corey and Bill.
Tim I emailed you, Bill Ill go theer as soon as I post this, Corey, thanks for the offer, with bill and timmys info i shouldnt need it but many thanks just the same. must still be lighting fine as i have not recieved any follow up calls. But i will be returning to clean the fire box and anything else that this info sheds light on.
Thanks again!
pipewrench0
This discussion has been closed.
Categories
- All Categories
- 87.5K THE MAIN WALL
- 3.3K A-C, Heat Pumps & Refrigeration
- 59 Biomass
- 429 Carbon Monoxide Awareness
- 124 Chimneys & Flues
- 2.2K Domestic Hot Water
- 5.9K Gas Heating
- 118 Geothermal
- 168 Indoor-Air Quality
- 3.8K Oil Heating
- 78 Pipe Deterioration
- 1K Plumbing
- 6.6K Radiant Heating
- 394 Solar
- 15.9K Strictly Steam
- 3.5K Thermostats and Controls
- 56 Water Quality
- 50 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements