GB142 design question
JimmyJam
Member Posts: 78
I am quoting a large building with radiant floor heating system.
Can I put (2) GB142 (with manifolds) in "series" with some type of staging control?
Thanks!
71Gibby
Can I put (2) GB142 (with manifolds) in "series" with some type of staging control?
Thanks!
71Gibby
0
Comments
-
yes
But, I don't think you can do it in series, rather parallel, and supply and return piping may need to be increased off pre-piped manifolds.
The sizes and piping configurations are listed in their applications manual.
See if you can get a copy of that.0