Burner won't lite
ozone357
Member Posts: 9
Burner won't lite. Utica SFH6225 with Beckett CF375. Set burner to spec per Utica 2.00x45B @140PSI. One caveat is that there is an air boot. Only way to get burner to lite is to close that air gate to 30%. I tried to clean the fire up but the burner won't lite afterwards.
0
Comments
-
What is your head setting
http://www.uticaboilers.com/pdfs/1003038rev1SFH-W&SADDENDUM.pdf The other trick is to get it running set the air band and shutter and move the head to adjust flame.0 -
Burner wont light
Call us, 1-800-OILBURN, or email me cmasone@beckettcorp.com
Charlie Masone
RW Beckett0 -
burner wont light
when you close down the air and then it lights what kind of smoke are you getting with a smoke tester?
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
things to chk
Not to sound stupid but did you check your transformer ,nozzle ,nozzle assemble and last but not least your electrode gap maybe your elctrodes are to advanced and when the true air band setting is in place it's blowing the spark gap.Check tranny and electrodes hows the porcleans looking ?Don't loss faith peaceand good luck clammyR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements