Dole 1933 replaced with a Gorton # D as main Vent

Cast Iron
Member Posts: 35
So after reading Dan's books and visiting the wall, I replaced the Dole 1933 on my 2"X 18' main with a Gorton #D. The main now fills with steam very quickly, in about 3 minutes from when the header gets hot.
Here is my question, although the main and return are hot (approx 210* according to my infra red thermometer) the Gorton does not get hot enough to close. Is this normal? I suspect that once the main fills with steam, the steam then goes off into the risers, etc. Which is why the Gorton never gets hot enough to close. After quite a while,I think when all the rads are hot, the Gorton will close.
Here is my question, although the main and return are hot (approx 210* according to my infra red thermometer) the Gorton does not get hot enough to close. Is this normal? I suspect that once the main fills with steam, the steam then goes off into the risers, etc. Which is why the Gorton never gets hot enough to close. After quite a while,I think when all the rads are hot, the Gorton will close.
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements