enerjet boiler
Rodney Summers
Member Posts: 748
im a hvac tech,i have a enerjet boiler with a problem.there is two gas burner tubes,the one to the left is not firing correctly.the flame comes out the front of the tube.i have seen this happen with a crack,rotted,or clogged tube but this one looks perfect.nat gas pressure is 3.5",draft is -4 at breach,-1 before draft diverter.boiler flues are clear although left passage has signs of soot.i think tube is defective has anybody seen this before.
0