One pipe steam (install into new addition?)

Steamhead (in transit)
Member Posts: 6,688
Minimum pitch is 1 inch in 10 feet, more is fine. Also, use the next size larger pipe than you would for a parallel-flow main. And be sure the take-off is above the required "A" dimension.
With the above done right, it'll work great. But you know that.
Is this the one for which you were asking about the small-tube rads?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
With the above done right, it'll work great. But you know that.
Is this the one for which you were asking about the small-tube rads?
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=367&Step=30">To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"</A>
0
Comments
-
When installing a new Steam main when the water is traveling in the opposite direction as the condensate can you pitch the pipe too much?
Jamie
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
steam
YES,, the condensate needs to able to stay on the bottom or side of the pipe so that it does not drip into any steam. If you run copper on new laterals, run at least 1 1/4',as 1" does not allow enough space w/ steam velocity and condensate return, the copper seems to react differently than steel pipe. Steam was made only to work w/ steel pipe, copper wasn't discovered yet.
0 -
Steamheat!
Steamhead! This is the job where we are adding 6 Burnham slenderized radiators into a new addition. The homeowner wanted the simplicity of one heating system for the entire house. The boiler was only about three years old but it was piped incorrectly. Once we convinced them that we could make the original house work they where gunho for the new section to match.
I read in one of our steam books not to use anything smaller then 2" when running a steam main is this just good practice? We ended up running about 40' of 2" steel to get into the new crawl space and then 20' in the crawl space that pitches back to the wet return in the original part of the house.
I'll post some pictures today!
0 -
Be sure
to vent the heck out of that new main! Unless those 6 Slenderized rads are way big, 2-inch should be fine.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements