New oil burner safety feature
Steve_35
Member Posts: 546
Now that we have primary controls that lock out in as little as 5 seconds it seems like the relay you mention would add more cost, reduce reliability and offer little in the way of benefit.
0
Comments
-
A proposed new oil burner safety feature . .
Last week I wrote about an igniter failure on my oil burner. I would like to ask you professionals if there is a good reason NOT to use a "current relay" or equivalent that would lock out the burner motor (or oil solenoid valve)should there be no primary current for the igniter or ignition transformer? What good could possible come from spraying oil into the combustion chamber when there is, and cannot be, a source of ignition?0 -
I can see where that might help
on larger burners- 5 seconds is a lot of oil on these.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
Properly maintained
My experiance has shown a clean and serviced unit with existing controls is all thats necessary.
Resets should only be pushed once as we all know homeowners only push once RIGHT??
Terry0 -
Already done
Riello's prove spark. Larger oil burners prove pilot.
All the best
Robert
ME0 -
once had a guy push the little red button 96 times he counted.0 -
This is a new one on me, Robert.
> Riello's prove spark. Larger oil burners prove
> pilot.
All of the Riellos I've seen prove flame only.0 -
Just goes to prove
no matter how idiot proof you make something, they'll always come up with a better idiot.0 -
Riello
All Riellos prove spark before oil valve can open.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements