excessive boiler pressure

JSPAK
Member Posts: 25
got a burnham residential boiler .pressure at stand still 12psi...temp starts to get to 170 ...pressuregoes up to 25....checked out expansion tank (extrol) was ok .... dissconnected tank and opened valve to meke sure boiler water getting to tank..was ok .... air pressure in extrol was 18 psi ..... changed presure reducing valve ..evenshut that off after pressure up to 12 psi in boiler ..... isolated domestic hw coil .... not that ...manually opened up taco zone walves still does it grrrrr .
0
Comments
-
Tank
Tank too small .0 -
cant be tank
i installed this boiler 6 years ago and been working ok ..with the tank that was there ..... i even tried installing a new tank yesterday .. same size0 -
pressure
change gauge, check, then put in larger tank0 -
I'm with you
With the water pressure at 25 and the tank air pressure at 18, that pressure difference is being made up by the diaphram. It seems too small or something else is going on. Did you check all the guages for accurate readings?
jerry
0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 940 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements