primary/secondary piping diagrams with dual boilers
siggy
Member Posts: 79
Here's another option if you need lots of DHW and can't find an indirect with enough heat exchanger capacity. The key is not creating any bottlenecks to heat transfer of flow betweent he boiler array and the tank.
Siggy
Siggy
0
Comments
-
primary/secondary piping diagrams with dual boilers
does anyone have any good piping diagrams for a primary/secondarypiping arrangement using 2 gas boilers and large 120 gallon indirect hot water heater.
thanks in advance!!
jim f
tri-city heating and cooling
milford, ct0 -
pri/sec pics
hope these help.0 -
P/S piping dual boilers
same as p/s piping single boiler app. one question what will control the boilers? Taco pc702 will do a good job because the load will not always need both to fire.
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
go to thread called piping buffer tank
there is a sketch showing a primary loop with a boiler and a buffer tank. Just pretend the buffer tank is a boiler and both are pumping into the primary loop0 -
A few way to do this
how many loads? What temperture? I'd pipe condensors different from convential. Here are some ideas.
http://www.pmengineer.com/CDA/ArticleInformation/coverstory/BNPCoverStoryItem/0,2730,83529,00.html
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
thanks for the reply,
i have 2 126,000 gas fired direct vent boilers to provide 4 hydronic air handlers approx 40-80k btus each, 40k btu for hydronic space heater in garage and a 120 gallon indirect hot water heater. manifolds will also have 2 future zones if needed.
i am starting to design my headers so i can have them fabricated by earthlee. my big thing is i want to make sure my indirect is taken at the right place.
so far my design will employ 2" main with first tee being 2" for the indirect and 14 1" secondary supplies
jim f
tri-city0 -
Some more info
http://www.pmengineer.com/CDA/ArticleInformation/coverstory/BNPCoverStoryItem/0,2730,17213,00.html
I'll attach a pic of figure 5 since it didn't make the online version. Notice how the indirect plumbs in this drawing. Also the high temperature loads up on top right.
Keep in mind every take off will see a lower temperature with a row of closely spaced tees on a header. This may or may not be an issue for the last set of tees?
You could pull the indirects of a parallel loop also, instead of the primary loop. This is shown in #5
Now, if you need all the secondary loads to see the same temperature, a parallel primary loop would be better. A lot more pump and piping needed. Crude drawing
hot rod
To Learn More About This Professional, Click Here to Visit Their Ad in "Find A Professional"0 -
high capacity DHW
Here's another option if you can't find an indirect with enough heat exchange capacity. the key is not creating bottlenecks to flow or heat transfer betweent he boiler array and the tank.
Siggy0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements